C5/B5/A4-Series f/w 6.71.02.0008 L2 Querier state Transitions between Non-Querier and Querier
  • Article
  • Updated 5 years ago
  • (Edited)
Article ID: 15105
Products
C5-Series, firmware 6.71.01.0067 and higher
B5-Series, firmware 6.71.01.0067 and higher
A4-Series, firmware 6.71.01.0067 and higher
Changes
Enabled IGMP Snooping with L2 Querier election; for example on VLAN 196:
set igmpsnooping adminmode enable
set igmpsnooping querier enable
set igmpsnooping 196 enable
set igmpsnooping querier 196 enable
set igmpsnooping querier 196 address 10.26.196.23
set igmpsnooping querier election participate 196 enable
Deployed two or more such systems into the network, so that they negotiate for the Querier role.
Symptoms
Each non-querier system cycles between Non-Querier and Querier states; remaining Non-Querier for about 60 seconds, briefly moving to Querier, then reverting back to Non-Querier to repeat the cycle.
For example:
    C5(su)->show igmpsnooping querier detail
Last Querier
VLAN ID Address IGMP Version
196 10.26.196.1 v2
197 10.26.197.1 v2
198 10.26.198.1 v2
199 10.26.199.1 v2
Global IGMP Snooping querier status
IGMP Snooping Querier Mode Enable
Querier Address 0.0.0.0
IGMP Version 2
Querier Query Interval 125
Querier Expiry Interval 60
VLAN 196 : IGMP Snooping querier status
IGMP Snooping Querier VLAN Mode Enable
Querier Election Participate Mode Enable
Querier VLAN Address 10.26.196.23
Operational State Non-Querier
Last Querier Address 10.26.196.1
Operational version 2
Operational Max Resp Time 11
Operational State Querier
C5(su)->
Cause
The Querier Expiry Interval (default 60 seconds) should not be less than the Querier Query Interval (default 125 seconds).
The Querier Expiry Interval is expiring all local knowledge of a previously established active querier before the Querier Query Interval triggers that active querier to send out a general query refresh. As a result, there is a period of time when this Non-Querier becomes what it believes is the sole Querier, resulting in multiple queriers on the VLAN.
Solution/Workaround
To be corrected in a future firmware release.
Contact the GTAC for an update, as necessary.
Workaround:
On each affected system, issue the command 'set igmpsnooping querier timer expiry 255', which will make the local device the querier only if the previously known querier is no longer performing that function.