Not receiving the right trap when EAPS ring change

JohanHendrikx
Contributor II
When one link of my eaps links went down I noticed that the switch sends the trap: extremeEapsLastStatusChangeTime and there was no alarm in Netsight.

In Netsight the alarm is triggerd by extremeEapsLinkDownRingComplete.

Is this correct ?

Johan Hendrik System Architect Audax
9 REPLIES 9

Michal_Rz
New Contributor III
Where did you select this traps? In Netsight 7.0 there are ony traps with word "eaps' in as shown in image.

3cf8b8c7389a48ceb7316c76eaf47cb6_RackMultipart20160805-56571-kejjag-eaps-netsight_inline.png



And when I selected extremeEapsLastStatusChangeTime alarms goes wrong, it send message Ring down when it goes up. Or in 6.3 it was working and 7.0 aint?

Also cant find any place where i can define my own traps.

edit:
found solution
https://gtacknowledge.extremenetworks.com/articles/Q_A/Trap-definitions-from-Netsight-6-x-are-not-vi...

JohanHendrikx
Contributor II
Thanks Sephen
Johan Hendrik System Architect Audax

StephenW
Extreme Employee
Johan,

extremeEapsStateChange would be the best trap to use. Looking at the MIB I found that the "extremeEapsLinkDownRingComplete" trap will only be sent when If a EAPS Transit node is in a Link-Down state, and it receives a Health-Check-Pdu from the Master indicating the ring is complete. This should not happen in a correctly configured EAPS ring, and is why you didn't receive this trap.

Sorry for the confusion and hope this helps.

Stephen

JohanHendrikx
Contributor II
Stephan,

Different swtiches (X450a-24t and X450a-24x) Firmware is 15.2.1.4-patch1-44

I use now the trap extremeEapsStateChange to trigger the alarm

Johan Hendrik System Architect Audax